Search the forum,

Discuss Testing RCBO x5 times in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello everyone,
Is it necessary to test RCBO x5? Some say that you can’t even test at x5 times because it can damage RCBO. Others that you can, but we don’t put the result in testing sheets. I found a recommendation that it is advisable to test x5.
Cheers
 
I wouldn’t expect an rcbo to be damaged by a leakage test unless the current was in the Ka region not the mA region.
remember that the current normaly would be a multiple of the rcd trip current I.e. 30mA x 5 = 150mA or in technical terms the grand total of F-All current.
 
The concern was raised about the multiple switching on/off rather the level of current, which could reduce the lifetime of the device, if the whole range of tests were performed on AC and A settings. Hence the requirement to test only on AC and only the 1x test.

To answer the OP question - the wiring regulations BS7671 only require the 1x test to be performed on the setting for type AC. There's nothing to stop us from doing the 5x test for our own piece of mind though.
 
There seems to be many spurious reasons given for the change in RCD/RCBO testing, but I think the true reason was to make testing quicker & cheaper.

No, you will not damage a RCBO testing it at 5*In as @James points out that is something like 40,000 times smaller than the rated ultimate breaking capacity.

No, you will not wear it out either under any sane regime. Looking at a typical data sheet (ABB came up first in google) they often are rated for 10,000 electrical cycles (i.e. operating at rated load of tens of amps) or 20,000 mechanical cycles (operating with negligible load).

If your traditional test was two 'In' trips (0 deg/180 deg), two '5*In' trips, and a test-button trip, along with maybe initially isolating for other tests, that is 6 cycles. To wear it out you would need to do that 3,333 times. If you did that test on every working day in a year (around 200) it would take you 16 years.
 

Reply to Testing RCBO x5 times in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
792
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
417
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
950
Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock