Currently reading:
Volt drop question and advice

Discuss Volt drop question and advice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Hi, I'm looking for a bit of advice on a volt drop query we have in our office.

I'll explain the scenario and I would really appreciate any opinion's and advice.

We were asked to wire a 3ph 100A supply into a barn, that would later be used to feed a new build house. The meter and supply comes into a GRP at the site boundary. We installed 125m of 50mm 5 core SWA from here into a distribution board in the barn. The volt drop was coming back at approx 2.4%. At the time of installation the details of the new build house were unknown.

Now a third part electrician has come into look at the site and the proposed new house. They are saying that the supply is too small based on VD and he is suggesting it should have been a 95mm!

95mm seems overkill to me. They are claiming that 2.4% plus the supply to the house, plus the final circuits is going to add up to more than the 3% allowed for lighting, but it still doesn't sit right with me.

My question really comes down to.. Can we use diversity in relation to VD when sizing cables like this? I feel like there needs to be some common sense brought into the equitation, but unsure how I can put this across to the client and refer it back to the regs.

Many thanks in advance.
 
Volt drop is calculated from source to the furthest point on any final circuit. If you have 2.4% solely on your submain then the chances are there is going to be excessive volt drops on these final circuits.
 
Volt drop is calculated from source to the furthest point on any final circuit. If you have 2.4% solely on your submain then the chances are there is going to be excessive volt drops on these final circuits.
Volt drop is calculated from source to the furthest point on any final circuit. If you have 2.4% solely on your submain then the chances are there is going to be excessive volt drops on these final circuits.

Agreed. Do you think it is reasonable to use diversity, based on the fact a house will never use 100A at 415v?
 
Agreed. Do you think it is reasonable to use diversity, based on the fact a house will never use 100A at 415v?
Surely that will depend on what is connected to it. And the nominal voltage between phases is 400V (+10%/-6%).
 

Reply to Volt drop question and advice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock