Discuss What do these ratings mean in the UK Electrical Forum area at ElectriciansForums.net

diyer1

DIY
Reaction score
2
Hi,

I was looking at my dishwasher and it has this metal plate with these markings.
20240428_085936.jpg


I am confused about the meaning of "10/16A" - does that mean it uses a 10A fuse or a 16A fuse?
Also, I am guessing that there are two sets of values (230V - 2,3kW - 10/16A vs 240V - 2,5kW - 13A). I wonder how you know which fuse it should use, given that
"In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts".

Just curious, not doing any work on it :)
 
In simplistic terms the resistance is constant but power (kw) will change proportionately with the applied voltage. So for 230v the power is 2.3kw and for 240v it is 2.5kw. The 10A fuse satisfies 230v and the 16A fuse satisfies 240v, I suspect 13A fuses which would satisfy both is not included as they are generally unique to the UK.
 
Thanks.

The 13A is there, after the // mark. So I think that indicates that he 13A is appropriate for 2.5kW at 240V, which makes sense.

So, where it says 10/16A, that means that either 10A or 16A can be used? It's just confusing, 10A should be enough, so why even mention 16A.
 

Reply to What do these ratings mean in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am curious about voltage ratings on wire. I'm interested in 10-4 for a 25-foot cord that will be carrying 25 Amps at 240 volts. There are two...
Replies
13
Views
1K
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
992
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
480
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hi folks, new member here. I am a DJ/electronic music producer with basically zero experience in advanced electronics. I recently bought the...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock