Discuss What kind of cable to run 400 amp residential service 625 feet in the UK Electrical Forum area at ElectriciansForums.net

bondonian

DIY
Reaction score
0
Hello Everyone,
I am building a new home in Illinois and will be running 400 amp service from the street where the main ComEd electrical line is located to my house. Here is the problem, or at least what im worried about, the house is over 600' from the main ComEd line. My question is, what type of cable is going to be required to run that amperage over that distance? i did some quick research and i think the answer is, THE VERY EXPENSIVE KIND, but i read enough that i knew i should come in and ask someone who has experience with this stuff. What i was finding was that i might need a cable called 900 MCM. I am not sure what that is, but i know it is expensive. Is that the type of cable i'll need? are there any other ways to reduce the cost of the run?

Thanks in advance, i appreciate your time and any information you can share.

Mike
 
Hello Everyone,
I am building a new home in Illinois and will be running 400 amp service from the street where the main ComEd electrical line is located to my house. Here is the problem, or at least what im worried about, the house is over 600' from the main ComEd line. My question is, what type of cable is going to be required to run that amperage over that distance? i did some quick research and i think the answer is, THE VERY EXPENSIVE KIND, but i read enough that i knew i should come in and ask someone who has experience with this stuff. What i was finding was that i might need a cable called 900 MCM. I am not sure what that is, but i know it is expensive. Is that the type of cable i'll need? are there any other ways to reduce the cost of the run?

Thanks in advance, i appreciate your time and any information you can share.

Mike
Can you just parallel 3/0 copper, in other words that would be four 3/0 for the live phases 2 neutrals. Make sure that you tape the red phases and the other 2 phases leave them black and white tape your neutrals. Do not cross your phases.
 

Reply to What kind of cable to run 400 amp residential service 625 feet in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I don't have much room around my current 200 amp panel and want to upgrade to 400 amp. I'd have an electrician do the work but I am just trying to...
Replies
1
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
hello. i need to run power to a cabin that is 350 feet from the service pole in our driveway. the problem is voltage drop. the service pole is 150...
Replies
8
Views
1K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hello --- In the planning stages for a new custom home build -- The house will be several hundred feet from the road and I want to have the power...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top