Search the forum,

Discuss Changing main RCD AC-type to A-type in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD feeding all the circuits in the consumer unit is AC type. Based on this, I believe I have to change this to an A type which is fine but the question is, do I then have to test every individual circuit in the building as I have changed the characteristics of each circuit? This obviously would change an hour job into a job that could take considerably longer, particularly if there are faults on other circuits and of course have cost implications to the customer. Could anyone offer any advice on this please? Many thanks in advance.
 
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD feeding all the circuits in the consumer unit is AC type. Based on this, I believe I have to change this to an A type which is fine but the question is, do I then have to test every individual circuit in the building as I have changed the characteristics of each circuit? This obviously would change an hour job into a job that could take considerably longer, particularly if there are faults on other circuits and of course have cost implications to the customer. Could anyone offer any advice on this please? Many thanks in advance.
I'd test the sockets ZS & RCD trip time and lighting. You're quite right it's altered the whole installation but testing a percentage of it should be adequate enough in my opinion.
 
I meant more to do with circuit connection than the RCD as such you'd at least want to make sure things worked before walking away as you may have to undo a bus bar and anything connected to the original AC type.

In an ideal world you'd only need to undo four screws.
 
like for like replacement. (even though its slightly different)
Just test the circuit with the addition, and the new rcd trip time, as required for the test cert.

If it mattered at all, it would have been already thought of, would be clear cut instruction, and you wouldn't have to ask the question.
 
I meant more to do with circuit connection than the RCD as such you'd at least want to make sure things worked before walking away as you may have to undo a bus bar and anything connected to the original AC type.

In an ideal world you'd only need to undo four screws.

If you can obtain a compatible RCD this is fine. No I would not check all the other circuits.
The trip times are for the RCCB, so testing it once will give you those. They're not circuit specific.
like for like replacement. (even though its slightly different)
Just test the circuit with the addition, and the new rcd trip time, as required for the test cert.

If it mattered at all, it would have been already thought of, would be clear cut instruction, and you wouldn't have to ask the question.
Hi all, thanks so much for getting back to me. You've all been really helpful, Maurice
 

Reply to Changing main RCD AC-type to A-type in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
910
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
1K
i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
931
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
329

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock