Might be a silly question, but can a tt supply come into a property via underground .
This property in question, has no overhead cables supplying it but looks like it might have an earth electrode somewhere.
Thanks.
 
Have you any photos?

While I have never worked on them, I have seen terraced houses in London that were TT supplies fed from what looked like normal underground cables.
 
20240308_122736.jpg
 
Last edited:
The earth cable on the right of met, just dissappears into the ground with the service cable apparently.
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
 
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
I can't seem to view the pic but if it is 6.0 this doesn't mean too much.
 
Can't help wondering what the separate RCCB is supplying.

Has all the hallmarks of an electric shower with no overcurrent protection, although the round cable suggests I could be wrong.
 
Yes it is possible to have an underground TT supply. Any supply can be made TT if required.

However it more than likely has an earth connection available that nobody has yet taken advantage of.

Contact the DNO to check the availability of an earth.
 
Yes it is possible to have an underground TT supply. Any supply can be made TT if required.

However it more than likely has an earth connection available that nobody has yet taken advantage of.

Contact the DNO to check the availability of an earth.
Thanks, yes they are getting a survey from Dno to see what can be done.
 
I would be a bit shocked if it is a TT system in.
looking at the area it looks like NEW BUILDS there (within a few years)


"The new wording within Regulation 411.4.2 is the final paragraph, where it introduces a recommendation that an additional connection to Earth by means of an earth electrode to the main earthing terminal. ." Taking for Napit site
i did notice the Sticker 25/08/23 and i wonder how old the house is

(hope this is within this site rules)
 
Last edited:
I would be a bit shocked if it is a TT system in.
looking at the area it looks like NEW BUILDS there (within a few years)
Don't link-build like that mate just stick the url in your signature on the forum and post normally please.
 

Reply to Is it a tt supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
910
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
534
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock