Discuss TT supply for static caravans in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
Need some advice, I have 7 static caravans to connect which need to be connected via TT

1. All the vans have a 30ma RCD main switch internally

2. All the vans come with a 2.5mm artic flex ready for connection

3. All vans will be connected through an double pole isolator switch

4. There is a new 100a 3phase PME supply ready

Here are my two options;

A - Convert the mains into TT, install a 100ma time delayed RCD and connect vans

B - Leave the PME supply up to the caravans and install an earth rod for each van

Thoughts?
 
I would go with (A) but obviously check you main earth rod is good enough and not close to any PME buried stuff (bonded water pipes, etc)
 
I would go with (A) but obviously check you main earth rod is good enough and not close to any PME buried stuff (bonded water pipes, etc)
It’s definitely my preferred option, I just worry that somehow to 30ma internally may cause the 100ma to trip
 
That's what I would do.
It is six of one and half dozen of the other.

PME to the supply RCD is easy and allows OCPD disconnection so simpler DB to feed it all. But then you need to meet 5s disconnection on those feeds and depending on cable length, etc, that might be a problem.

Going up-front RCD makes that aspect simpler as sub-main R1+R2 no longer a real issue and potentially higher OCPD for a bit of over-current selectivity with feed point OCPD, but easier for one fault to take out the lot. And you still need 30mA MCB/RCD or DP RCBO at each point.
 

Reply to TT supply for static caravans in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
555
Am I over thinking this, Pitch socket for caravan TT system 16 amp MCB, Rcd protection 30ma, supply 2.5 flex to DB in caravan also RCD...
Replies
6
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock