Discuss MBPC to caravan sizing in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
Am I over thinking this, Pitch socket for caravan TT system 16 amp MCB, Rcd protection 30ma, supply 2.5 flex to DB in caravan also RCD protected.
What’s the requirements for the MBPC for the caravan,minimum requirement 6mm to the DB MET
With the supply cable 2.5mm flex this is not achievable, unless the earth electrode is situated at the caravan & not the pitch socket, or is it acceptable for connection at the DB
 
Am I over thinking this, Pitch socket for caravan TT system 16 amp MCB, Rcd protection 30ma, supply 2.5 flex to DB in caravan also RCD protected.
What’s the requirements for the MBPC for the caravan,minimum requirement 6mm to the DB MET
With the supply cable 2.5mm flex this is not achievable, unless the earth electrode is situated at the caravan & not the pitch socket, or is it acceptable for connection at the DB
Obviously the pitch socket doesn't need main bonding.
Inside the caravan, regulation 721.411.3.1.2 applies -
"Structural metallic parts which are accessible from within the caravan shall be connected through main bonding conductors to the main earthing terminal within the caravan."
544.1.1 requires a minimum 6mm² main bonding conductor.
 
Obviously the pitch socket doesn't need main bonding.
Inside the caravan, regulation 721.411.3.1.2 applies -
"Structural metallic parts which are accessible from within the caravan shall be connected through main bonding conductors to the main earthing terminal within the caravan."
544.1.1 requires a minimum 6mm² main bonding conductor.
Agree but the actual supply would only be a flex cable….
So if it’s a 100amp supply, 10mm MBPC required, It’s a TT system at the pitch socket, from that point would you take a MBPC to the caravan from there, to comply
 
Agree but the actual supply would only be a flex cable….
So if it’s a 100amp supply, 10mm MBPC required, It’s a TT system at the pitch socket, from that point would you take a MBPC to the caravan from there, to comply
No.
The pitch socket has a separate earthing system, being TT.
The main bonding conductor needs to be not less than half the size of the earthing conductor of the TT system, subject to a minimum size of 6mm².
 

Reply to MBPC to caravan sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
910
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
934
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock