Am I over thinking this, Pitch socket for caravan TT system 16 amp MCB, Rcd protection 30ma, supply 2.5 flex to DB in caravan also RCD protected.
What’s the requirements for the MBPC for the caravan,minimum requirement 6mm to the DB MET
With the supply cable 2.5mm flex this is not achievable, unless the earth electrode is situated at the caravan & not the pitch socket, or is it acceptable for connection at the DB