To meet 5% voltage drop at 32A you need 10mm, for a more realistic 13A load it is 4mm.
There are three sizing requirements for cables:
There are three sizing requirements for cables:
- Current carrying capacity (CCC) to avoid overheating
- Voltage drop (VD) so end loads are operating within expected tolerance
- Earth fault impedance (Zs) to make sure Automatic disconnection of Supply (ADS) is met sufficiently fast depending on the circuit protection (fuse/MCB, use of RCD)