Search the forum,

Discuss No earth electrode visible? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
21
Hi all,

Carrying out a periodic inspection at a domestic installation. Semi- detached house on a row of houses. I cannot for the life of me locate any sign of the earth electrode inspection chamber. Just wondering how you would number this? A 1,2,3 or a 4?

Thanks
 
You need to establish the property has a reliable and safe means of earthing. Can you visually trace the earth? What size is the main earth at CU?

Is Irish EICR coding different to mainland uk?
 
You need to establish the property has a reliable and safe means of earthing. Can you visually trace the earth? What size is the main earth at CU?

Is Irish EICR coding different to mainland uk?
Hi Richy.

Thanks for the reply. I can't trace that cable as it disappears down behind the wall the DB is mounted on.
The main earth coming from suppliers cut out is 10sq.

Yes the coding is different, as we number it 1-4 in terms of the risk involved
 
Hi Richy.

Thanks for the reply. I can't trace that cable as it disappears down behind the wall the DB is mounted on.
The main earth coming from suppliers cut out is 10sq.

Yes the coding is different, as we number it 1-4 in terms of the risk involved
you say there is a main earth from the supply cut-out. does that mean it's been upgraded to PME? what's the Ze?
 
Is Irish EICR coding different to mainland uk?
Irish regulations are different to UK regulations.
you say there is a main earth from the supply cut-out. does that mean it's been upgraded to PME? what's the Ze?
Yes it will be TNCS but under Irish regulations an earth electrode is also required.
 
Assuming the installation is neutralised, I would give a 2 to an Earth electrode which could not be located as it is impossible to verify that it is correct (or even present). A simple test doesn't prove this.
 
Assuming the installation is neutralised, I would give a 2 to an Earth electrode which could not be located as it is impossible to verify that it is correct (or even present). A simple test doesn't prove this.
Thanks Risteard. I had put it down as a 2, even though I wasn't sure if I was right in doing so. Good to hear you'd have done the same. Thanks for the reply
 

Reply to No earth electrode visible? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
395
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
797
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
385
Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Replies
16
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top