Search the forum,

Discuss Supply question in the Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i wanted to see where its supplied from and origin etc. It turns out the Electrician has wired the sub mains board from an old redudant 3 phase power line. Hes run 16mm 6181y protected by a RCD. cable runs outside up the pole and connected to the lines.
Then at the sub board there is is 4 core 10mm swa connected to the lines down to the sub mains board.
Surely this is a big No No and needs disconnecting.
 
Not easy to figure out what is going on here,
what exactly is your concern?
is the cable underrated for the protection,
is there a lack of earth?
is the cable (redundant? or now in use) in poor condition?
 
If it is bare wires, separated by air. then assuming it is in good condition, I cant see an issue unless it could come in to contact with something.
have a look at 417.3
have a think, have you identified a risk or a deviation from the regs.
or is it just something you have not seen before and are thinking it must be wrong because it is unusual?
 
If it is bare wires, separated by air. then assuming it is in good condition, I cant see an issue unless it could come in to contact with something.
have a look at 417.3
Will do thanks. The manager did say , a tipper truck did catch it once, even though he told him hes close, he said no it will be fine. And yep apparently caught one of the lines 🙈.
 
If it is bare wires, separated by air. then assuming it is in good condition, I cant see an issue unless it could come in to contact with something.
have a look at 417.3
have a think, have you identified a risk or a deviation from the regs.
or is it just something you have not seen before and are thinking it must be wrong because it is unusual?
Yes not seen before and wondered if was allowed. Poles may belong to DNO etc. So just wondered if it was allowed . That is all .
 
If it is bare wires, separated by air. then assuming it is in good condition, I cant see an issue unless it could come in to contact with something.
have a look at 417.3
have a think, have you identified a risk or a deviation from the regs.
or is it just something you have not seen before and are thinking it must be wrong because it is unusual?
Just read 417.3 👍🏻. Puts my mind at rest.
 
Have you got any photos? I'm picturing something really horrific here.
 
Have you got any photos? I'm picturing something really horrific here.
No sorry, but its just a pole with 5 horizontal lines 3ph N E . Which go across to, two other poles , between old barns , then a phase dropped down to one board and 3 phase supply dropped down to another fused board , SWA used from the lines down to the boards. All protected by 32amp 60898 with linked 61009 RCB0.
 
If a fork lift has already hit it then placing out of reach is somewhat tenuous and a means of protection I have never resorted to in 40 odd years.
 
Years ago it was not uncommon to install private overhead lines for distribution circuits in places like farms, caravan parks, industrial sites.

It may be that these days it is no longer suitable for that site and it could attract a C2 code should an EICR be carried out. But this shouldn't have any bearing on you installing a fire alarm.
 
If a fork lift has already hit it then placing out of reach is somewhat tenuous and a means of protection I have never resorted to in 40 odd years.
Farm lads around here run into LV overheads all the time, seems ‘placing out of reach’ was never really considered with 20’ flail mowers in mind!!
 
I'm picturing LV overhead lines feeding a 3ph DB in a barn (BS 6181's) and in turn from there feeding another 3ph DB.
just a pole with 5 horizontal lines 3ph N E . Which go across to, two other poles , between old barns , then a phase dropped down to one board and 3 phase supply dropped down to another fused board , SWA used from the lines down to the boards. All protected by 32amp 60898 with linked 61009 RCB0.
And SWA cables feeding other 'boards' !! from the overhead lines ........ but where is the metering unless it is a private distribution network and metering is at source/intake? and whole lot protected by 32A mcb?
 
This sounds to me like Barns with the customers overhead connections after the intake and metering.
There used to be many like this near me, with uninsulated conductors running on poles between the Barns.
Most of them now have been changed to underground supplies due to the exact problem above.
As tractors and equipment has got bigger they have become more likely to be struck by such equipment and as a result installed in a much safer way!
 
And SWA cables feeding other 'boards' !! from the overhead lines ........ but where is the metering unless it is a private distribution network and metering is at source/intake? and whole lot protected by 32A mcb?

Yes, relatively common, especially in rural areas, once upon a time.
The bare overhead lines would be hard-drawn copper and supported on porcelain insulators.
PILC, SWA or insulated and sheathed tails would be connected to them via line taps wherever required.

I suspect this type of distribution is the reason, or at least one of the reasons, that 'placing out of reach' is still in the regulations as a method of protection.
Much like BS3036 fuses and PEN conductors, you can't just remove the regulations that support them because they still exist in the real world despite being out dated.
 

Reply to Supply question in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
183
190m run SWA underground, supplied from 3p+N 240mm sub main, each cabin total demand is 80A, worked out 35mm but volt drop is about 8%, would this...
Replies
9
Views
734
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
534
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top